Click for Northern Lights Click for Delta Click for Glendinning Click for YF Listing Service Click for CL Yachts
New to chillers
Discussion in 'HVAC' started by Danvilletim, Jun 16, 2018.
  1. Danvilletim
    Danvilletim Senior Member
    isleton, ca
    our new boat has chillers rather than the older spilt systems.
    The salon is not cold enough and the staterooms are very cold.
    Any suggestions on getting the salon cooler? Boat has 2 chillers that can be operated together or one at a time ?
    What air temps are blowing from the salon system?
    Lots of air blowing?
    Lots of windows and sunshine?
    Ensure the servo driven water valves are working at each station correctly with it's zone thermostat.
    I would not call them high maintenance but they do require an eye ball a couple of times a year. They do get stuck. The leading cause of issues.
    Very often if the chilled water is not treated.
    If the salon unit is the top (older) system, may (MAY) have air trapped in it's coils. There should be a bleed nut on the top of the coils.
    Ensure around 15PSI water charge. Crack the nut to ensure all water and no air comes out.
    Recharge the chilled water and pressure back to 15PSI or what the mfg spec states after the bleed.
  3. captainwjm
    captainwjm Senior member
    Miami, FL, Cape Elizabeth, ME
    That’s it.
  4. Pascal
    Cruisair systems have servo valves to send chilled water thru the air handlers. If the air out of that handler isn't cold enough and you can feel that the evaporator isn't getting cold then chances are the valve isn't opening when ordered to by the tstat.
    They also have a little metal tab you can push to open it manually.
    Obviously make sure both chillers are coming on. Again it depends on the system you have Cruisair has a digital control panel installed near the chillers
    Which will show status and error codes.
    In cooler weather you can run on one chiller but not at this time of the year although sometimes with iffy shore power at night you can run on a single chiller.
    Such a better system than the splits. I installed a Flagship Marine two chiller system on my boat and love it.
  5. Capt Ralph
    Would he really need both chillers on line for non severe (hot as heck) operation?
  6. captainwjm
    My 65’ Pacific Mariner was built in Washington state and only has one chiller. It does the job for us, but later models were built with 2 chillers specifically for the Florida/Carribean market. My guess is that he can get cool enough with one unit depending on how much glass he has, and what type of shades he uses.
  7. Pascal
    Assuming the system was set up with both chillers in parallel serving the whole boat in mild weather you don't need both. Or at night as I mentioned. Or if you re not using all the rooms. You can turn off some air handlers or keeping them at a high setting so the cooling power goes to the salon and whatever room is being used. The flexibility and redundancy is what make chillers a great set up
  8. Capt Ralph
    OH YES.
    Let get the servo valves on the air handlers checked like we said.
  9. Capt J
    Until the raw water pump or circulating pump go bad or you lose a hose and you lose everything.
    Check temps at air handlers and try bleeding them a little and see if any air comes out of the line. Check temps at each air handler. You might have to install an additional air handler and the salon most likely is at ththe end of the loop. Measure loop temp at each unit.
  10. Pascal
    You don't loose everything because you have valves to isolate various circuits. And it s a lot easier to fix a failed water hose than a leaking gas line ...
    Most split system share a water pump anyway... I always carry both circulation and raw water spares.
  11. Capt Ralph
    Negative Vibes, To many Negative Vibes. *
    Hoses come off the other A/C systems also. Pumps go bad also.
    Good boy scouts keep spares.
    I would hope the taller (more exposed) air handlers are first in the loop.
    * My Donald Sutherland gig for those that remember...
  12. Flybull
    Flybull New Member
    Branson
    "There you go with them negative waves again, Moriarity...!!" :)
  13. PacBlue
    PacBlue Senior Member
    Dana Point, Ca
    I need to rent Kelly's Hero's and watch it again...
  14. Capt Ralph
    One of our fall / winter treats is looking up old fav movies. Yep, gona pull Kellys Heros back up this year.
    Shame they dont make entertaining movies any more.
  15. Capt Ralph
    Stack of old Bogart movies planed also.
  16. bayoubud
    bayoubud Senior Member
    Florida
    We have two Aqua Air chillers...#2 chiller had low pressure about 8 weeks ago... turned breaker off because of bringing boat back from Stuart to the Fl panhandle. Last week the #2 chiller was checked and had a freon leak in the condenser. Got a estimate to replace #2 and the next day #1 had low pressure reading and had the same problem. The mfg'r says they were probably being cleaned with corrosive materials. The original chillers lasted nine years...the current chillers lasted seven years. Not good longevity... So, be careful to use the right solution is being used to clean system.
  17. f3504x4ps
    f3504x4ps Member
    Cape Canaveral, FL
    For the water lines do you run antifreeze/water mix or stright water with an additive?
  18. Pascal
    I run straight water. In places where it can freeze in winter I think they run an anti freeze mix.
  19. bayoubud
    Florida
    Not sure what is in our lines...we have owned this boat since May and other than filters and cleaning air handlers have not needed maintenance till now. They a/c tech will be taking old chillers out next week, so we should know then.
  20. captholli
    captholli Senior Member
    In The Bilge
    Your AC tech will recommend you to run 10% food grade Glycol in your chilled water loop and it's used not so much for freeze up but rather a better solution for thermal transfer from your chiller plates. Some Marine Glycols come with a fluoresced tracer dye for finding leaks which can come in handy. You'll be surprised to see how dirty "loop" water becomes after a few years especially if your chiller has immersion heater elements.