Discussion in 'Technical Discussion' started by RAchten, Jun 10, 2015.

You need to be registered and signed in to view this content.
  1. RAchten

    RAchten Guest

    Hi All

    My new Carver has two 30amp inlets (one for HVAC and one for everything else). Since in my limited cruising experience I have noticed I only get one outlet at most Marina's, I think my solution to this should be to get a slip with a 50amp outlet, then have a y adapter that splits it down to (2) 30 amps to lead into my boat. My questions:

    1) Is this the best solution to get the most power to my boat, given no access to (2) 30 amp outlets?
    2) In your experience, do most Marinas have the 50amp / 125 v or the 50amp / 125-250v power source? I guess it makes a difference in the type of y adapter I purchase.

    Thanks in advance ;)
    Rich
  2. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,149
    Location:
    Miami, FL
    On the east coast 125/250-50 is pretty much standard in most slips (except small ones) not 125/50 although it may still be found at some small, back water places...
  3. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,434
    Location:
    Fort Lauderdale
    I agree with this as well, 250V 50amp is common almost everywhere. I cannot even remember where I've even seen 125v/50amp. You should have no problems using a Y adapter to go from 250V/50 to 2-125v/30amps and it's very common to do that.
  4. NYCAP123

    NYCAP123 Senior Member

    Joined:
    Mar 14, 2008
    Messages:
    11,205
    Location:
    Long Island, NY
    Generally you'll find just one 30 amp outlet only by slips for small boats. like under 26'. Almost anywhere you go you should have (2) 30 amp outlets available If one is too distant ask the dockmaster. They can generally locate another cord to get you connected. 50 amp outlets are generally at slips for boats over 42' or so. The only 50/125s I've run into were at a county marina on FIre Island, and commercial docks.
  5. TeKeela

    TeKeela Member

    Joined:
    May 1, 2012
    Messages:
    151
    Location:
    NC & Puerto Rico
    50amp/125 is often an RV setup.
  6. todd_raleigh

    todd_raleigh New Member

    Joined:
    Jan 9, 2023
    Messages:
    1
    Location:
    Vero Beach, FL
    Hi. I'm new to all this. If you use a Y-adapter (50 Amp, 125/250V) as described above, are you actually getting full 30Amp/120V on each leg? or does it share 50Amp across both L5-30R legs?
  7. SplashFl

    SplashFl Active Member

    Joined:
    Feb 2, 2021
    Messages:
    431
    Location:
    S. Florida _ Bertram 46
    50 amp at 250 v. would be 100 amp at 125 v. so there is more then enough of the 250 available when splitting to 2 30's.
  8. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,727
    Location:
    Satsuma, FL
    Err, Ahh, Ohh,,,, NO

    Your 240V/50A out let uses two x 50 amp breakers for each 120V leg that make the 240V.

    So, there is 50A at each 120V/30A outlet when split.
    Later boats have a service breaker near the boats connect and the main panel breaker to help to still keep it a 30A system.
    MBevins likes this.
  9. SplashFl

    SplashFl Active Member

    Joined:
    Feb 2, 2021
    Messages:
    431
    Location:
    S. Florida _ Bertram 46
    My dock pedestal has two 30 amp 120 v. breakers tied together feeding a 50 amp female 220 v. receptacle where the boat is plugged in and homes main breaker panel where it feeds from has a double 30 amp 220 v. breaker.
    Previous boat took two 30 amp feed lines so electrician only had to change the pedestal breaker and replace the two 30 amp receptacles with the one 50 amp 220.
    Breaker size is determined by size of feed wire in my case, 30 amp as each wire is #10.
    Last edited: Jan 9, 2023
  10. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,727
    Location:
    Satsuma, FL
    Yes, that would provide 220v at 30 amp per 115v leg.
    That single 50A breaker is actually dual 50s tied together side by side.
    If one leg tries to trip, it brings the other leg open with it.
    Un-like the separate 30s that if one would trip, the other would remain hot.
  11. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,727
    Location:
    Satsuma, FL
    Wire size and length.
    So from your house to dock is #10 or #6 wire?
  12. SplashFl

    SplashFl Active Member

    Joined:
    Feb 2, 2021
    Messages:
    431
    Location:
    S. Florida _ Bertram 46
    It's #10 as the plans called for, the electrician ran, and the city inspector passed. For some reason a splice box was put on the back wall before the wires go into the underground conduit to the dock pedestal. I know it's 10 as many years ago I tapped into one of the two hot legs & the neutral adding a 20 amp inline fuse and then a 20 amp GFI receptacle via a short piece of # 12; probably against code for some reason, but I saw nothing wrong with it and it's been a very handy receptacle for several decades.
    Also back when I had the 38, her zincs were vanishing in like 4-6 months so one year I brought in the local big name marine electric company to find the cause. After running all of their tests found nothing wrong they installed a Galvanic Isolator on the boat after its 30 amp breaker on the always plugged in line and after that zincs lasted "forever." In her 30 years here before selling, she never had any electrolysis issues and so far the diver has been reporting the single underwater zinc on the 46 is still in good shape but its only been 6 months.