    Well, I finally hit a marina (Titusville Municipal) with 'new' GFI pedestals that tripped when hooking up my shore power. I went through the standard troubleshooting.

    1. turn everything off on boat (inverter, all individual breakers and main shore power breaker)
    2. hook up shore power
    3. turn on pedestal (no trip, so shore power cord OK)
    4. turn on main breaker at boat, shore power pedestal immediately trips

    I talked to 5 different mechanics, none of whom seemed confident they could not diagnose and resolve the issue. It could be anything from a bad ground who knows where to incorrectly wired inverter or appliance. One guy told me there was nothing wrong with my boat, I just needed to buy an isolation transformer. The one guy (electrical engineer and ABYC cert) who was an expert at this was not available. I moved to another marina for the night and decided to wait until I can get a knowledgeable to take a look.

    So, does anyone know of an ABYC certified electrical mechanic/electrical engineer type who really knows how to troubleshoot this problem on the AICW north of FL? I think a really good guy could identify the issue relatively quickly, but someone not very experienced in this could spend all day ($$$) troubleshooting with no resolution.

    We're nearing Savannah now and headed up to NY to do the Down East Loop. I'm more interested in finding the right guy than getting it looked at soon.

    thanks!
  2. PacBlue

    PacBlue Senior Member

    Joined:
    Jan 9, 2009
    Messages:
    1,988
    Location:
    Dana Point, Ca
  3. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,725
    Location:
    Satsuma, FL
    I did not see step 5 above. All other breakers off when main breaker on.

    Have to realize what is happening. Current on the green line.
    You probably have green and white wires tied on board.
    First cause of this is a green strap on the gen-set or inverter. Next their tied behind the service panel.
    Do you have an updated schematic on board?
    What brand/model boat ?
  4. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,149
    Location:
    Miami, FL
    A marine inverter only bond G to N when in inverter mode. If you have a non marine inverter (RV or off the grid) it will be the issue.

    the generator could be the issue as it bonds G and N. If your boat uses a double pole breaker, I guess G and N will stay bonded at all time. If your panel uses a rotary switch which also disconnects N, then it should not be a problem

    i believe ABYC doesn’t allow G to N bonding except at the source (shore, inverter or gen) so there should be no connection at the electrical panel

    the culprit is likely to be an appliance. Oven, cook top, washer, dryer etc. to eliminate them, disconnect the plugs. Turning off the breaker won’t help because the neutral will still be connected to the boat therefor shorepower and possibly bonded to G
  5. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,725
    Location:
    Satsuma, FL
    Remove power, no current should flow.
    I forgot Hatts use single pole breakers. Berts use dual & triple pole breakers.
  6. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,434
    Location:
    Fort Lauderdale
    I deal with a boat that has a GFCI on the main shorepower breaker in the boat, I've had it trip if A/C water pan got clogged and full of water.....or with an ice maker when the compressor was starting to go bad.

    With everything off, turn off every single A/C breaker in the boat, then turn the main breaker on, then turn each individual breaker on until you find the circuit that trips the GFCI on the dock.

    As for a marine electrician in Savannah, I do not know. Perhaps call Thunderbolt boat yard and they might have one working for them or can refer you to one.
  7. d_meister

    d_meister Senior Member

    Joined:
    Mar 4, 2010
    Messages:
    469
    Location:
    La Conner, WA.
    There are a couple of boat yards in Savannah Bend that very likely have expert help available. I've stayed at Hinckley Yacht Services in the past, but had no work done there. There's also a bigger yard there at Thunderbolt that does a lot of big boat work.
  8. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,725
    Location:
    Satsuma, FL
    If your spending any time in StAug or Jax on your way north, I think I can get a tech on board.
  9. mapism

    mapism Senior Member

    Joined:
    Aug 9, 2008
    Messages:
    2,115
    Location:
    Sardinia
    I'm going to make a few assumptions, based on my understanding of what you are saying in your OP:
    1) everything in your electrical system works fine when connected to a shore outlet which is NOT protected by a GFCI device;
    2) the same goes when you are connected to the onboard generator, or if you are drawing AC from the inverter(s);
    3) you do NOT have a master GFCI device onboard, downstream of the main breaker.

    If the above is correct, I would think that there is indeed something wrong with your boat, and you just didn't know.
    As a premise (which I'm making just in case), GFCI devices are meant to sense any circuit imbalance, potentially created by an accidental current leak through a human body, anywhere along the electrical circuit. In which case, by cutting the power immediately, a GFCI device can actually make the difference between life and death.
    Now, the most common standard in Europe for these devices is to cut power at 30 milliamps of current leak, but I'm not sure about the US. There are devices capable to sense leaks as low as 10 or 5 mA.
    Trouble is, even 30 mA is actually a pretty small leak in absolute terms - not to mention 10 or 5.
    On the other hand, the device MUST cut power immediately upon a small leak, otherwise it wouldn't achieve its purpose of protecting from severe electrocution.

    So, let's say that your socket in Titusville marina is protected by a 10 mA GFCI device.
    If my initial assumptions were correct, you might have always had a total leak of say 12 mA, and that is enough to trip the 10 mA device, even if everything works perfectly whenever you are connected to a non-protected shore power.
    And mind, your 12 mA leak could well be due to a sum of several different leaks, like 4 mA in the cooktop, 6 in the heater, and another 2 elsewhere (it's almost impossible to have zero current leaks, in any somewhat complex electrical circuit).
    For this reason, it would be appropriate to have a master GFCI device also onboard, to protect the whole electrical circuit also when powered by the genset, and regardless of whether the shore power is protected or not.

    Back to troubleshooting.
    The leak is obviously downstream of your main breaker, otherwise the shore power would trip off upon step 3 of your list.
    This rules out not only the shore power cord, but also the segment of your electrical circuit that goes from the cord to the electrical panel.
    Which is kind of a pity, because often the culprit, in boats where the power cord is attached to an onboard external socket, is in the socket itself, that can get wet inside due to weather exposure.
    And in this case, it's just a matter of opening the socket, dry it out, and possibly use some spray electrical insulating sealer.
    But this should not be the case in your boat.
    So, what remains to be checked is which segment of the circuit generates more dispersion.

    Now, I agree with Capt Ralph when he mentioned the "step 5" which is missing from your list.
    In fact, I suppose that before turning on the main breaker in your step 4 you did NOT turn off all the single breakers downstream of it.
    If you did, there's no logical reason why the shore GFCI should trip off, and that would be very weird indeed.
    On the other hand, I don't agree with Pascal when he suggests that it's necessary to physically disconnect all appliances.
    A GFCI device should not trip off unless there is a current imbalance, and there can't be any when a breaker is off, even if single pole (which imho should have no place on a boat, anyway), because there is no current absorption at all.
    So, assuming that the shore doesn't trip off if you turn on the main breaker with all other breakers off, it should be sufficient to turn them on one at a time, to identify one culprit.

    Mind, I'm saying ONE culprit because you could as well have more: in my previous example, if you disconnect the cooktop with its 4 mA leak, you would still have 8 mA residual leaks (6 in the heater + 2 elsewhere). Not enough to trip the 10 mA GFCI device, but the 6 mA leak in the heater would still be worth fixing.
    But for this type of troubleshooting, it's necessary to open the electrical panel, have a leakage clamp meter, and know how to use it.
    I can explain this further if you are interested, but that's something better left to a specialized electrician.
    Also because, to complicate things further, the leaks I previously used just as an example can actually change, depending on whether the connected appliance is turned on or not, and also other factors like the relative humidity in the air - go figure!

    Sorry for the long post, but I hope it can help.
    Good luck, anyhow!
  10. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,781
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Has anyone been doing any " home made" wiring ?
  11. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,781
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Current electric Pedestals have 30 or 40 Ma GFCI breakers ( equipment protection ) as opposed to GFCI breakers or outlets in a home which are 5 Ma. ( personnel protection ) point of use.

    A marina owner had a customer whose boat tripped the pedestal GFCI immediately and he was pretty PO'd about it.
    He insisted that the marina power was goofed up and his boat was not at fault.

    His boat tripped every pedestal it was plugged into, eliminating a faulty GFCI Breaker.

    When asked the question if any wiring had been done on the boat he admitted to some " cabling" he did himself.

    End of story is a piece of his cable that was hot, connected to nothing and had slipped into the bilge where water had accumulated.

    All of his insults to the marina, marina electrician, power company, pedestal company were forgotten .......
  12. motoryachtlover

    motoryachtlover Senior Member

    Joined:
    Jan 29, 2007
    Messages:
    651
    Location:
    smithfield, VA
    Kalakai, Hinckley Yachts in Savanah (Thunderbolt) had a very good marine electrician. His name was Michele (French). I don’t know if he is still there. I had Hinckley Savanah do a fair amount of work on boat about 5 years ago on 2 different occasions. They did nice work and at he quoted price. Provided they have the same GM (Dustin??) I have no reservations recommending them. Also I had a small job done by Thunderbolt marine and I had a good experience there as well.
  13. KalaKai

    KalaKai New Member

    Joined:
    Sep 30, 2016
    Messages:
    7
    Location:
    New Orleans
    Thanks very much for all of the replies. I'm not much of an electrician, so it's going to take some time to digest/understand all of this info. I'm away from shore power for a few days, so won't be able to trouble shoot now. I'll see if anyone in Savannah can take a look. I'll call one of the bigger yard, but still would appreciate any specific names there, or further north who are 'experts' on this subject.

    to answer a few questions raised
    * Don't have wiring schematic, Navigator 53 is the boat
    * already north of Jax, so need someone at, or north of Savannah
    * all downstream breakers were off when I turned on main boat breaker
    * there are no 220v appliances on the boat
    * I don't have, or know how to use, a clamp type meter

    Thanks again to all who tried to help out

    cheers!
  14. PacBlue

    PacBlue Senior Member

    Joined:
    Jan 9, 2009
    Messages:
    1,988
    Location:
    Dana Point, Ca
    I know all the Navigators usually had Galvanic Isolators installed and a fairly clean and robust grounding system. But I imagine the dealer or aftermarket electronics guys have tapped into the factory wiring at some time. Best get a savvy electronics onboard to walk you through the process.
  15. mapism

    mapism Senior Member

    Joined:
    Aug 9, 2008
    Messages:
    2,115
    Location:
    Sardinia
    This is very puzzling ideed.
    In principle, in a properly designed electrical panel, in between the main breaker and each line-specific breaker there should be ...ermm... nothing!
    I mean, after the main breaker you should have simply some shortish wires, feeding each of the downstream breakers.
    In best designed panels, this is often done through connecting bars rather than wires, but that's just a detail.
    In any case, it should be practically impossible that any current dispersion develops just by turning on the main breakers, with ALL the downstream breakers off.

    This leads me to think that either the electrical panel was not designed with these basic principles in mind, or someone played with it afterwards and made some changes/additions to the connections.
    And since I have no reason to doubt what PB said in his last post about Navigator boats usually having a clean and robust elec system, the latter of these two alternatives seems the more likely.

    Either ways, not something for which you can get any further help from anyone through a forum, I'm afraid.
    Next step is bound to be have someone who knows his onions opening the electrical panel and putting his eyes and hands on it.
    Just a hint: if he doesn't show up with a leakage clamp meter (which shouldn't be such an exotic tool for a good electrician, but I've seen some of them who don't have one, just because somewhat expensive and not so frequently used), look for someone else.
  16. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,434
    Location:
    Fort Lauderdale
    Check your shorepower wiring connections from the cable to where it attaches in the boat and at the back of the breakers. I've seen many that were loose after years of use.
  17. PacBlue

    PacBlue Senior Member

    Joined:
    Jan 9, 2009
    Messages:
    1,988
    Location:
    Dana Point, Ca
    I would suspect that if the boat has a Grill and/or Washer/Dryer than you have 240VAC Appliances onboard, you would typically see two 120VAC legs tired together on the AC Breaker Panel.
  18. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,725
    Location:
    Satsuma, FL
    I had one DIY owner install a new Glendinning shore cable. Somehow, he got green and white wires tied together. He argued they were tied together in his house. Check your service inlet breakers and strapping.
  19. CSkipR

    CSkipR Member

    Joined:
    Aug 16, 2008
    Messages:
    965
    Location:
    New Smyrna Beach, Fl
    In my case it was the old style galvanic isolator 2005 had an issue and tripped the new St Aug marine power pedestals. Electrician disconnected the wire on the old isolator at the marina and all was well. Got home installed new galvanic isolator about $300.
  20. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,781
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    And the galvonic isolator in your boat was connected BEFORE the main breaker or after ?

    Mine is before.