Hi guys. I am new kid on the block for yachts, and appreciate your help. I have a 95 carver aft cabin with twin 350 crusaders my ac will work for a while then the screen on the thermostat reads CDL I am pretty sure that is what is was. I am not positive. Both units are doing it. Can anyone suggest anything I can try before looking for a specialist?
If both units run off one pump then that would be where I would start since you said both units have the same readout.
I've never seen a CDL error, usually it's HP, LP or LO AC. Check the pump and check the air conditioning strainer, those usually have to be cleaned often.
Are you familiar where the water exits the boat after it circulates through the ac units? If so, are you getting water flow? If not check for blockage at sea strainer. Check to see if pump is running.