Shore Power Problem

Discussion in 'Technical Discussion' started by Albert Jewitt, Jun 5, 2016.

You need to be registered and signed in to view this content.
  1. Albert Jewitt

    Albert Jewitt New Member

    Joined:
    Oct 7, 2015
    Messages:
    1
    Location:
    Longport Seaview, New Jersey
    I have a live aboard 43' Vista Motor Yacht, which has a single 50 ampere 220 volt service.
    I had no problem with my Shore Power for years, while I was in the water.
    Pulled the boat last week for routine maintenance.
    I was able to hook up to a full electrical service, in dry dock.
    This was I can keep my chest freezer, refrigerator, battery charger & work power going.
    When I first hooked it up, one phase was reading 120 volt the other was reading 150 volt.
    I check the voltage at the source(panel), both phases read 120 volts.
    I turned the fluorescent lights on in my stateroom, they got real bright & the ballast smoked.
    I immediately killed all the power to the yacht.
    Has anyone had a similar situation?
    Looking for advice.
    Capt. Bert
  2. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    12,737
    Location:
    Satsuma, FL
    No or poor white wire (neutral) connect.
  3. justold

    justold Member

    Joined:
    Feb 23, 2009
    Messages:
    51
    Location:
    new jersey , fla
    x2
  4. Dan Thibault

    Dan Thibault New Member

    Joined:
    Jun 6, 2016
    Messages:
    3
    Location:
    Murrells Inlet, Sc 29576
    Are you feeding transformers with the 220 or do you really have 50Amp - 120/240v cable feeding the yacht??
    If transformer I would start looking there?