Cabo 40FB A/C issues

Discussion in 'Cabo Yacht' started by kxp086, Nov 29, 2011.

You need to be registered and signed in to view this content.
  1. kxp086

    kxp086 New Member

    Joined:
    Nov 25, 2011
    Messages:
    3
    Location:
    Lower Slower Delaware
    Hello all!.
    I am new to the forum, however, I have been boating for over 30 years. Last year I purchased a 2005 Cabo 40FB. After said purchase the salon deck A/C failed. Long story short, unit was replaced and ever since the cooling/heating ability has been sub par. A major mid-atlantic service yard has tried several times to make right, any suggestions?:confused:
  2. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,149
    Location:
    Miami, FL
    Hard to reply without more info. What failed? Compressor? You said "unit was replaced"... Normally on such a recent unit you re not going to replace the whole thing but just the compressor or evaporator

    What kind of AC if you have? Compact or remote compressor in the ER? On a 40 it s likely to be a compact but you never know..

    Subpar doesn't mean much.. Does it just not cool enough? It s not rocket science any decent AC tech should be able to put gauges on and see what a going on. What about water flow, is it strong enough? When is the last time the coils were descaled?
  3. kxp086

    kxp086 New Member

    Joined:
    Nov 25, 2011
    Messages:
    3
    Location:
    Lower Slower Delaware
    Thanks for the response, 16000 btu Cruisaire, compressor located in lazzerette under galley sole, pump was replaced at same time compressor was replaced. Original unit for state rooms, feeds off of same pump, that unit works great. Coils were serviced at the time all this was being serviced.
  4. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,434
    Location:
    Fort Lauderdale
    Chances are when the compressor died it sent a bunch of debris through the freon lines. If there is a filter/dryer in the evaporator chances are it could be clogged. Your going to have to measure the line temperature going in and coming out of the evaporator on the FB. It sounds like a freon restriction to me.
  5. captbluewater

    captbluewater New Member

    Joined:
    Mar 24, 2005
    Messages:
    27
    Location:
    Los Suenos
    You should also check the discharge of cooling water. You could have good pressure going to inlet side but maybe on discharge side there could be some clogging. It happen to me. A bunch of broken barnacle pieces.
  6. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,149
    Location:
    Miami, FL
    In addition to what capt J suggested, I would check water flow out of the unit There could be some blockage in that line. If you can't actually see that unit discharge pull the hose and put it in a bucket to see how much flow you get

    Any error codes on the display?