Battery Problem?

 
 
Thread Tools Rate Thread Display Modes
Old 03-22-2008, 01:49 PM   #1
Globetrotter76
Registered User
 
Join Date: Oct 2004
Location: In UK at the Moment and will be around St Marteen around mid December
Posts: 21
Battery Problem?

Hi Forum Peeps,

I need some advice regarding a battery problem on the new boat I have joined. There are 3 battery banks in the engine room one for each generator and main engine. The two for the Generators are maintenance free. The one for the main engine is lead acid battery. They are setup as two 12v in series to provide 24v………..

They are all linked to a Lewco Battery Charger.

The batteries are hooked up onto a monitoring system so that I can monitor the charge of the batteries at all time.

I found that the battery for the Main Engine is constantly sitting at 30v on my monitoring screen, whereas the other 2 batteries cycle from 27v to 30v as they are on charging cycle

I checked the battery compartment and felt for heat and there was none, I then checked the water levels and they were low and all cells on both batteries were low so I then proceeded to top them up, I still see no change……..after 2 days

I have attached a picture from the monitoring screen so u can see the trend…..

Why is this battery staying at 30v constanly,
Battery Info Nominal Voltage 12v Each
Cold Cranking Amps – 1100
Cranking Amps – 1230
Amp Hours – 200

Is this a problem? Should I replace the battery bank? Any further comments?
Attached Images
Globetrotter76 is offline   Reply With Quote
Old 03-24-2008, 01:51 PM   #2
Highlander
Registered User
 
Join Date: Sep 2007
Location: Milford Boat Works CT
Posts: 32
Batteries are a pain

Globetrotter,

Are there any loads on? Sensors? Any load will cause the charger to react.

Unless the charger is designed to handle two different battery types, you have a problem there.
are the maintenance free bateries, gell cells or AGM ?
The charger must be set to the native voltage for each type of battery.

As batteries age they will not be able to get up to full voltage and the charger may keep the voltage high, thinking they need a charge, when in reality the water is boiling off. How old are the batteries? Anything over three years is getting old. All the modern AC converters do is kill batteries.

Have fun

Carl
Highlander is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are EST. The time now is 06:43 PM.

Click for Burger
Click for Burger
Click for NorthCoast
Click for Shadow
Click for Dyna
Click for Horizon


Powered by vBulletin Version 3.5.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 2.3.3