Diesel Electric Superyacht

 
 
LinkBack Thread Tools Rate Thread Display Modes
Old 11-18-2010, 03:39 PM   #1 (permalink)
Registered User
 
Join Date: Nov 2010
Location: Southampton
Posts: 5
Diesel Electric Superyacht

Hi, I am currently designing the powering/propulsion system of a superyacht as a project at university and I have run into numerous problems.

1) The yacht will have 3 CAT gensets providing up to 5,500kw and a minimum of 1300kw. If the yacht requires only 850 kW when at anchor for hotel loads and stabilizers it would not be efficient to run 1 genset at 1300kW as power would be wasted. Would the best solution be to have a separate aux. generator?

2)solar panels are also to be used as a renewable source of energy, can their power simply be added to the switchboard?

3)Does anyone know of any simple calculations for hotel loads and fresh water stores per person/time at sea for superyachts?

thanks!
stavsantis is offline   Reply With Quote
Old 11-18-2010, 04:27 PM   #2 (permalink)
AMG
YF Moderator
 
AMG's Avatar
 
Join Date: Jul 2004
Location: Sweden
Posts: 4,932
Hi, if you are sure the yacht will need 850 kW at anchor, a 1300 kW genset is probably what you need. But I guess both figures should be lower and that you install 2 additional gensets with the right size.

Solar panels can be added to the grid, but is a waste of space on such a power consuming yacht.

On average consumption, I have no figures, it depends on climate and facilities onboard.
AMG is offline   Reply With Quote
Old 11-18-2010, 04:34 PM   #3 (permalink)
Registered User
 
Join Date: Nov 2010
Location: Southampton
Posts: 5
others have told me that 600kW is alot however, from a paper written for modern superyachts it quoted a hotel load of 600kw for an 80m yacht....
stavsantis is offline   Reply With Quote
Old 11-18-2010, 04:36 PM   #4 (permalink)
AMG
YF Moderator
 
AMG's Avatar
 
Join Date: Jul 2004
Location: Sweden
Posts: 4,932
OK, how big is your project yacht..?
AMG is offline   Reply With Quote
Old 11-18-2010, 04:37 PM   #5 (permalink)
Registered User
 
Join Date: Nov 2010
Location: Southampton
Posts: 5
75m so i assumed it would be the same
stavsantis is offline   Reply With Quote
Old 11-18-2010, 04:57 PM   #6 (permalink)
AMG
YF Moderator
 
AMG's Avatar
 
Join Date: Jul 2004
Location: Sweden
Posts: 4,932
I think you would be fine with two 500 kW gensets and a small emergency generator (fitted on the upper deck), besides what you need for the propulsion.
AMG is offline   Reply With Quote
Old 11-18-2010, 06:22 PM   #7 (permalink)
Senior Member
 
Join Date: Jul 2005
Location: Fort Lauderdale
Posts: 5,694
First, you should design the yacht and calculate all of it's load sources such as air conditioners, ovens, refrigeration, then decide on generators. I would choose 2 generators, where 1 generator can run everything on the entire yacht. Then it's possible to get a 3rd generator that is 75% of the output of the other 2 and can be used during lighter load periods. I've found though, that it is rare that you're not pulling close to the same load all of the time, unless it's 70 degrees outside (PNW) and you're not running any air conditioning/heat
Capt J is offline   Reply With Quote
Old 11-19-2010, 04:03 AM   #8 (permalink)
Senior Member
 
K1W1's Avatar
 
Join Date: Sep 2005
Location: My Office
Posts: 6,283
Quote:
Originally Posted by stavsantis
others have told me that 600kW is alot however, from a paper written for modern superyachts it quoted a hotel load of 600kw for an 80m yacht....
Hi,

Did the Author have any real life experience of superyachts other than seeing them from the dock?

You should make a list of all your electrical equipment as previously suggested and then get a load balance calculation done by a marine electrical engineer.

Building an 80m Motoryacht that is going to cruise extensively with only 2 Main Gensets is short sighted at best. If you use main 3 Gensets you can have one out of action for maintenance etc and still have full functionality.

I am doing an 80m boat now with 3 x 435 Ekw Gensets and a 120 Ekw Emergency Genset. It's sistership needs approx 280 Ekw when underway with the normal range of hotel services on offer and peaks up with the Galley. We need two sets on when manouvering as the thrusters can use nearly 600 between them at 100% capacity. The yacht was setup to run on one Genset most of the time and the first one has proven to do this and do it well, they have run 9000 hrs on the Gensets in 3.5 yrs and have no problems so far.
K1W1 is offline   Reply With Quote
Old 11-19-2010, 04:11 AM   #9 (permalink)
AMG
YF Moderator
 
AMG's Avatar
 
Join Date: Jul 2004
Location: Sweden
Posts: 4,932
K1W1, what do you think of using some power from the main gensets of 5.500 kW as backup? Or would you not connect those to the "hotel side" at all?
AMG is offline   Reply With Quote
Old 11-19-2010, 05:34 AM   #10 (permalink)
Senior Member
 
K1W1's Avatar
 
Join Date: Sep 2005
Location: My Office
Posts: 6,283
Quote:
Originally Posted by AMG
K1W1, what do you think of using some power from the main gensets of 5.500 kW as backup? Or would you not connect those to the "hotel side" at all?
Hi Lars,

The main stumbling block to sharing the drive bus and hotel services bus is the formation of Harmonic Distortion on the AC Sine wave that comes back of the Freq Controllers used to operate the drives. A lot of DE Installs are higher voltage and 60 Hz which does not suit a lot of Hotel Equipment.

If I were going to do it that way I would certainly look at the use of a Motor Genset driven by the Drives side of things and supplying the Hotel Services with Clean power. I have personal knowledge of one large DE Project where this has been done and it works very well according to the operational C/E and ETO.
K1W1 is offline   Reply With Quote
Old 11-19-2010, 01:38 PM   #11 (permalink)
Registered User
 
Join Date: Nov 2010
Location: Southampton
Posts: 5
as far as my knowledge on superyachts, evidently it is almost non existent, this is part of a 3rd year university project i have been assigned. for propulsion power i have chosen 3x3516B CAT gensets coupled to 2 pods. I can see that using solar power will not provide much power however the yacht specifications is for it to be as 'green' as possible so using some may help.

do you run the gensets for aux. power (hotel loads) 24hrs a day? or are they connected to batteries from which power can be used at lower loads?
if so what sort of batteries are suitable?

k1w1 - what voltages to you suggest i use for the hotel loads? 240v??

I apoligise for my ignorance in the field and any help would be useful
stavsantis is offline   Reply With Quote
Old 11-19-2010, 02:16 PM   #12 (permalink)
AMG
YF Moderator
 
AMG's Avatar
 
Join Date: Jul 2004
Location: Sweden
Posts: 4,932
Quote:
Originally Posted by stavsantis
I can see that using solar power will not provide much power however the yacht specifications is for it to be as 'green' as possible so using some may help.
If you must do a "green" yacht, forget about the thousands of kW and make something like this:
Attached Images
AMG is offline   Reply With Quote
Old 11-19-2010, 02:52 PM   #13 (permalink)
Senior Member
 
K1W1's Avatar
 
Join Date: Sep 2005
Location: My Office
Posts: 6,283
Quote:
Originally Posted by stavsantis
as far as my knowledge on superyachts, evidently it is almost non existent, this is part of a 3rd year university project i have been assigned. for propulsion power i have chosen 3x3516B CAT gensets coupled to 2 pods. I can see that using solar power will not provide much power however the yacht specifications is for it to be as 'green' as possible so using some may help.

do you run the gensets for aux. power (hotel loads) 24hrs a day? or are they connected to batteries from which power can be used at lower loads?
if so what sort of batteries are suitable?

k1w1 - what voltages to you suggest i use for the hotel loads? 240v??

I apoligise for my ignorance in the field and any help would be useful
Hi,

At least one of the Gensets will be running 24/7/365 unless you can get enough shore power or they are stopped for service/maintenance.

Why have you particularly chosen 3516 Engines and what is the rating of the ones you have chosen?

There is a very successful DE Yacht a bit bigger than what you are asking about that runs multiple smaller Gensets and two pods. The approx Power requirements are the same as your proposal.

You should try and get as much of your Hotel load as possible - AC, Galley, Laundry, Sewage Plant, Water Makers etc on 3 Phase Power. The single phase consumers are not that much in total and the whole phase balancing action is a lot more straight forward of you don't have to much single phase stuff on the system.
K1W1 is offline   Reply With Quote
Old 11-19-2010, 03:44 PM   #14 (permalink)
TheAdmiral
Guest
 
Posts: n/a
As well, you can estimate 800-1200 Watts/room for A/C depending on temp differential and humidity. Radar systems/GPS and other Cockpit electronics are easily calculable. Another 300W - 400W per person is a good rule of thumb for 10 people or more which would include direct usage plus refrigeration etc.

The big sporadic use systems such as Cranes/Pumps etc have to be estimated individually based on duty cycle.

Last edited by TheAdmiral; 11-19-2010 at 04:19 PM..
  Reply With Quote
Old 11-20-2010, 07:47 AM   #15 (permalink)
Senior Member
 
Marmot's Avatar
 
Join Date: May 2007
Location: 9114 S. Central Ave
Posts: 2,830
Quote:
Originally Posted by stavsantis
If the yacht requires only 850 kW when at anchor for hotel loads and stabilizers it would not be efficient to run 1 genset at 1300kW as power would be wasted.

Isn't anyone going to comment on this fundamental misconception?
Marmot is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On