Old 04-21-2009, 10:20 PM   #1
C4ENG
Senior Member
 
C4ENG's Avatar
 
Join Date: May 2006
Location: US East Coast
Posts: 261
Can it be saved?

I first experienced a burning electrical smell in the ER and went ripping through everything looking for the source until I found this..a loose wire conection on a 10 ton chiller compressor.. The compressor was still running when I found it. I cleaned it up a bit and cut back the melted wire before the photo trying to see how much damage there was.

Can a new conection block be fitted on this compressor for the supply wiring?

Do you think this compressor can be saved?
Attached Images
C4ENG is offline   Reply With Quote
Old 04-21-2009, 10:37 PM   #2
Dan Evans
Senior Member
 
Join Date: Jun 2007
Location: Port Townsend
Posts: 130
If it was still operating correctly when you found it then chances are its still good. However, when there is any doubt about something working out at sea would you really like to take the chance of it not turning on one day? I would have an electrician or Emerson technician take a look at it. Make sure you trace the wires to make sure that is the only damaged spot. Good luck!

Dan
Dan Evans is online now   Reply With Quote
Old 04-21-2009, 10:49 PM   #3
vornado
Registered User
 
vornado's Avatar
 
Join Date: Feb 2008
Location: Panama - Panama
Posts: 9
Quote:
Originally Posted by C4ENG

Can a new connection block be fitted on this compressor for the supply wiring?

Do you think this compressor can be saved?


That is a Hermetic compressor. A new connection block can not be fitted as far as I know. So, if the connection block is damaged ( I can not really see in the pic) you are out of luck.
vornado is offline   Reply With Quote
Old 04-21-2009, 11:21 PM   #4
Capt J
Senior Member
 
Join Date: Jul 2005
Location: Fort Lauderdale
Posts: 957
Try calling a place that rebuilds compressors, they might be able to weld a new post to it, or a new box..........
Capt J is offline   Reply With Quote
Old 04-22-2009, 12:29 AM   #5
wdrzal
Registered User
 
Join Date: Feb 2006
Location: Baltimore
Posts: 139
They do make a varity of replacement terminal repair kits. Some are as simple as a set screws that tightens on the pin or whats left of the lug. To some that need the electrical connections soldered on and then the entire connection is covered with a resin based putty (epoxy)that hardens to lend support making it permenant.

You can find these repair kits at refrigeration or HVAC specility shops.

Be sure to First get the nomenclature off the compressor & take it with you.(the line above the bar code that ends in 250). If you don't have the schemetics go to the Emerson site (bought copeland) and look up what the ohms between terminals is and test with a multimeter set to RX1. Also test for direct shorts (terminal to ground). More extensive testing can be done with a Megometer if you have one,this will test for leakage/damage of the internal electrical windings (state of the insulation).

Just from the picture I believe that compressor can be saved as long as their is no internal damage.
wdrzal is offline   Reply With Quote
Old 04-23-2009, 12:26 AM   #6
scott49
Registered User
 
Join Date: Mar 2008
Location: Woodinville,Washington
Posts: 75
One thing to also think about is not only can it be fixed but what caused it. You said loose connection, make sure that that was it. You don't want to put a new connection block (terminal repair kit) and have a fire later.
scott49 is offline   Reply With Quote
Old 04-23-2009, 01:03 PM   #7
wdrzal
Registered User
 
Join Date: Feb 2006
Location: Baltimore
Posts: 139
Scott is correct,you just can't assume it was a loose connection. Many times people fix a problem without finding the true cause. Other than a loose connection,too high superheat or un-balanced power supply or power supplied out of design parameters,loss of capacity should be high on the list,along with previous mentioned checks to verify the internal windings are OK.

I didn't mention that it is also possible to completly cut out the ceramic terminal block that passes through the shell & a new one welded in. This should be done by a professional. This requires refrigerant recovery,oil removal & shielding gases used for welding,then evacuation & recharge with oil and refrigerant. Keep in mind your working on a pressure vessel where high pressure gas and oil can be expelled. There is a rare occurance know as high pressure pin ejection,this happens when the ceramic is dammaged/cracked and there is still pressure inside the shell and the terminal is shot out like a bullet,it's very rare ,but does happen. So as long as the unit is charged becarful,wear safety glases and keep your body away from in front of the terminals.

You said the unit is 10 ton (120,000 btu), is that a single compressor or multiply units in a rack system. I ask becasue AFAIK all compressors over 5 ton are 3 phase. Severial small units may be single phase powered in tandem. They have capacitors and starting gear that also could be at fault.

One final note copeland on many of it's models offered long warrentys 5 to 10 years to get people to try scroll compressors. Some model lines had failure rates @~60%. Many of those were smaller units under 5 ton.
wdrzal is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are EST. The time now is 11:33 AM.

Click for Crescent
Click for Crescent
Click for Westport
Click for Christensen
Click for Moonen
Click for Quantum


Powered by vBulletin Version 3.5.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 2.3.3